bonjour a tous et merci pour tout votre travail deja effectuer ;
et bien je cherche a faire fonctionner une carte de chez dagu en modifiant le programme de sirnoname
X-Sim PID
This program will control two motor H-Bridge with analogue feedback and serial target input value
Target is a Arduino UNO R3 but should work on all Arduino with Atmel 328, Arduinos with an FTDI serial chip need a change to lower baudrates of 57600
Copyright (c) 2013 Martin Wiedenbauer, particial use is only allowed with a reference link to the x-sim.de project
Command input protocol (always 5 bytes, beginning with 'X' character and ends with a XOR checksum)
'X' 1 H L C Set motor 1 position to High and Low value 0 to 1023
'X' 2 H L C Set motor 2 position to High and Low value 0 to 1023
'X' 3 H L C Set motor 1 P Proportional value to High and Low value
'X' 4 H L C Set motor 2 P Proportional value to High and Low value
'X' 5 H L C Set motor 1 I Integral value to High and Low value
'X' 6 H L C Set motor 2 I Integral value to High and Low value
'X' 7 H L C Set motor 1 D Derivative value to High and Low value
'X' 8 H L C Set motor 2 D Derivative value to High and Low value
'X' 200 0 0 C Send back over serial port both analogue feedback raw values
'X' 201 0 0 C Send back over serial port the current pid count
'X' 202 0 0 C Send back over serial port the firmware version (used for x-sim autodetection)
'X' 203 M V C Write EEPROM on address M (only 0 to 255 of 1024 Bytes of the EEPROM) with new value V
'X' 204 M 0 C Read EEPROM on memory address M (only 0 to 255 of 1024 Bytes of the EEPROM), send back over serial the value
'X' 205 0 0 C Clear EEPROM
'X' 206 0 0 C Reread the whole EEPRom and store settings into fitting variables
'X' 207 0 0 C Disable power on motor 1
'X' 208 0 0 C Disable power on motor 2
'X' 209 0 0 C Enable power on motor 1
'X' 210 0 0 C Enable power on motor 2
'X' 211 0 0 C Send all debug values
EEPROM memory map
00 empty eeprom detection, 111 if set, all other are indicator to set default
01-02 minimum 1
03-04 maximum 1
05 dead zone 1
06-07 minimum 2
08-09 maximum 2
10 dead zone 2
11-12 P component of motor 1
13-14 I component of motor 1
15-16 D component of motor 1
17-18 P component of motor 2
19-20 I component of motor 2
21-22 D component of motor 2
23 pwm1 offset
24 pwm2 offset
25 pwm1 maximum
26 pwm2 maximum
27 pwm frequency divider (1,8,64)
Analog Pins
Pin A4 - input of feedback positioning from motor SCL
Pin A5 - input of feedback positioning from motor SDA
As well 5v and GND pins tapped in to feed feedback pots too.
#include <EEPROM.h>
#include <EEPROM.h> // library to access EEPROM memory
#include <IOpins.h> // defines which I/O pin is used for what function
// define constants here
#define startbyte 0x0F // for serial communications each datapacket must start with this byte
// define global variables here
byte mode=0; // mode=0: I2C / mode=1: Radio Control / mode=2: Bluetooth / mode=3: Shutdown
int lowbat=550; // default low battery voltage is 5.5V
byte errorflag; // non zero if bad data packet received
byte pwmfreq; // value from 1-7
byte i2cfreq; // I2C clock frequency can be 100kHz(default) or 400kHz
byte I2Caddress; // I2C slave address
int lmspeed,rmspeed; // left and right motor speeds -255 to +255
byte lmbrake,rmbrake; // left and right brakes - non zero values enable brake
int lmcur,rmcur; // left and right motor current
int lmenc,rmenc; // left and right encoder values
int volts; // battery voltage*10 (accurate to 1 decimal place)
int xaxis,yaxis,zaxis; // X, Y, Z accelerometer readings
int deltx,delty,deltz; // X, Y, Z impact readings
int magnitude; // impact magnitude
byte devibrate=50; // number of 2mS intervals to wait after an impact has occured before a new impact can be recognized
int sensitivity=50; // minimum magnitude required to register as an impact
void setup()
//Some speed test switches for testers ;)
#define FASTADC 1 //Hack to speed up the arduino analogue read function, comment out with // to disable this hack
// defines for setting and clearing register bits
#ifndef cbi
#define cbi(sfr, bit) (_SFR_BYTE(sfr) &= ~_BV(bit))
#endif
#ifndef sbi
#define sbi(sfr, bit) (_SFR_BYTE(sfr) |= _BV(bit))
#endif
#define LOWBYTE(v) ((unsigned char) (v)) //Read
#define HIGHBYTE(v) ((unsigned char) (((unsigned int) (v)) >> 8))
#define BYTELOW(v) (*(((unsigned char *) (&v) + 1))) //Write
#define BYTEHIGH(v) (*((unsigned char *) (&v)))
#define GUARD_MOTOR_1_GAIN 100.0
#define GUARD_MOTOR_2_GAIN 100.0
//------------------------- Define function of each I/O pin -------------------------------------------------
#define lmencpin 6 // D6 - left motor encoder input - optional
#define rmencpin 5 // D5 - right motor encoder input - optional
#define lmbrkpin 4 // D4 - left motor brake control pin HIGH = Brake
#define lmdirpin 2 // D2 - left motor direction control pin HIGH = Forward Low = Reverse
#define lmpwmpin 3 // D3 - left motor pulse width modulation pin 0 - 255 Speed and Brake
#define lmcurpin 6 // A6 - left motor current monitor pin 0 - 1023 -20A to +20A
#define rmbrkpin 9 // D9 - right motor brake control pin HIGH = Brake
#define rmdirpin 10 // D10 - right motor direction control pin HIGH = Forward Low = Reverse
#define rmpwmpin 11 // D11 - right motor pulse width modulation pin 0 - 255 Speed and Brake
#define rmcurpin 7 // A7 - right motor current monitor pin 0 - 1023 -20A to +20A
#define voltspin 3 // A3 - battery voltage 1V = 33.57 30V = 1007
#define axisxpin 0 // A0 - accelerometer X-axis
#define axisypin 1 // A1 - accelerometer Y-axis
#define axiszpin 2 // A2 - accelerometer Z-axis
//Firmware version info
int firmaware_version_mayor=3;
int firmware_version_minor =0;
int virtualtarget1;
int virtualtarget2;
int currentanalogue1 = 0;
int currentanalogue2 = 0;
int target1=512;
int target2=512;
int low=0;
int high=0;
unsigned long hhigh=0;
unsigned long hlow=0;
unsigned long lhigh=0;
unsigned long llow=0;
int buffer=0;
int buffercount=-1;
int commandbuffer[5]={0};
unsigned long pidcount = 0; // unsigned 32bit, 0 to 4,294,967,295
byte errorcount = 0; // serial receive error detected by checksum
// Pot feedback inputs
int FeedbackPin1 = A4; // select the input pin for the potentiometer 1, PC0
int FeedbackPin2 = A5; // select the input pin for the potentiometer 2, PC1
int FeedbackMax1 = 1021; // Maximum position of pot 1 to scale, do not use 1023 because it cannot control outside the pot range
int FeedbackMin1 = 2; // Minimum position of pot 1 to scale, do not use 0 because it cannot control outside the pot range
int FeedbackMax2 = 1021; // Maximum position of pot 2 to scale, do not use 1023 because it cannot control outside the pot range
int FeedbackMin2 = 2; // Minimum position of pot 2 to scale, do not use 0 because it cannot control outside the pot range
int FeedbackPotDeadZone1 = 0; // +/- of this value will not move the motor
int FeedbackPotDeadZone2 = 0; // +/- of this value will not move the motor
float quarter1 = 254.75;
float quarter2 = 254.75;
float threequarter1 = 764.25;
float threequarter2 = 764.25;
//PID variables
int motordirection1 = 0; // motor 1 move direction 0=brake, 1=forward, 2=reverse
int motordirection2 = 0; // motor 2 move direction 0=brake, 1=forward, 2=reverse
int oldmotordirection1 = 0;
int oldmotordirection2 = 0;
double K_motor_1 = 1;
double proportional1 = 4.200; //initial value
double integral1 = 0.400;
double derivative1 = 0.400;
double K_motor_2 = 1;
double proportional2 = 4.200;
double integral2 = 0.400;
double derivative2 = 0.400;
int OutputM1 = 0;
int OutputM2 = 0;
double integrated_motor_1_error = 0;
double integrated_motor_2_error = 0;
float last_motor_1_error = 0;
float last_motor_2_error = 0;
int disable = 1; //Motor stop flag
int pwm1offset = 50;
int pwm2offset = 50;
int pwm1maximum = 255;
int pwm2maximum = 255;
float pwm1divider = 0.8039;
float pwm2divider = 0.8039;
float pwmfloat = 0;
int pwmfrequencydivider = 1; //31kHz
byte debugbyte =0; //This values are for debug purpose and can be send via
int debuginteger =0; //the SendDebug serial 211 command to the X-Sim plugin
double debugdouble =0;
//========================================== Choose your desired motor PWM frequency ================================================//
// Note that higher frequencies increase inductive reactance and reduce maximum torque //
// Many smaller motors will not work efficiently at higher frequencies //
// The default is 122Hz. This provides relatively low noise and relatively smooth torque //
// This setting can be changed using I2C or Bluetooth //
// Thanks to macegr - http://forum.arduino.cc/index.php?PHPSESSID=n1691l4esq4up52krpcb77bgm1&topic=16612.msg121031#msg121031 //
//TCCR2B = TCCR2B & B11111000 | B00000001; pwmfreq=1; // set timer 2 divisor to 1 for PWM frequency of 31250.000000000 Hz
//TCCR2B = TCCR2B & B11111000 | B00000010; pwmfreq=2; // set timer 2 divisor to 8 for PWM frequency of 3906.250000000 Hz
//TCCR2B = TCCR2B & B11111000 | B00000011; pwmfreq=3; // set timer 2 divisor to 32 for PWM frequency of 976.562500000 Hz
//TCCR2B = TCCR2B & B11111000 | B00000100; pwmfreq=4; // set timer 2 divisor to 64 for PWM frequency of 488.281250000 Hz
//TCCR2B = TCCR2B & B11111000 | B00000101; pwmfreq=5; // set timer 2 divisor to 128 for PWM frequency of 244.140625000 Hz
// TCCR2B = TCCR2B & B11111000 | B00000110; pwmfreq=6; // set timer 2 divisor to 256 for PWM frequency of 122.070312500 Hz
//TCCR2B = TCCR2B & B11111000 | B00000111; pwmfreq=7; // set timer 2 divisor to 1024 for PWM frequency of 30.517578125 Hz
//Serial.begin(115200); //Uncomment this for arduino UNO without ftdi serial chip
//all IO pins are input by default on powerup --------- configure motor control pins for output -------- pwm autoconfigures -----------
pinMode(lmpwmpin,OUTPUT); // configure left motor PWM pin for output
pinMode(lmdirpin,OUTPUT); // configure left motor direction pin for output
pinMode(lmbrkpin,OUTPUT); // configure left motor brake pin for output
pinMode(rmpwmpin,OUTPUT); // configure right motor PWM pin for output
pinMode(rmdirpin,OUTPUT); // configure right motor direction pin for output
pinMode(rmbrkpin,OUTPUT); // configure right motor brake pin for output
pwmfreq=6;
#if FASTADC
// set analogue prescale to 16
sbi(ADCSRA,ADPS2) ;
cbi(ADCSRA,ADPS1) ;
cbi(ADCSRA,ADPS0) ;
#endif
void WriteEEPRomWord(int address, int intvalue)
int low,high;
high=intvalue/256;
low=intvalue-(256*high);
EEPROM.write(address,high);
EEPROM.write(address+1,low);
int ReadEEPRomWord(int address)
int low,high, returnvalue;
high=EEPROM.read(address);
low=EEPROM.read(address+1);
returnvalue=(high*256)+low;
return returnvalue;
void WriteEEProm()
EEPROM.write(0,111);
WriteEEPRomWord(1,FeedbackMin1);
WriteEEPRomWord(3,FeedbackMax1);
EEPROM.write(5,FeedbackPotDeadZone1);
WriteEEPRomWord(6,FeedbackMin2);
WriteEEPRomWord(8,FeedbackMax2);
EEPROM.write(10,FeedbackPotDeadZone2);
WriteEEPRomWord(11,int(proportional1*10.000));
WriteEEPRomWord(13,int(integral1*10.000));
WriteEEPRomWord(15,int(derivative1*10.000));
WriteEEPRomWord(17,int(proportional2*10.000));
WriteEEPRomWord(19,int(integral2*10.000));
WriteEEPRomWord(21,int(derivative2*10.000));
if(pwm1offset > 180 || pwm2offset > 180 || pwm1maximum < 200 || pwm2maximum < 200)
pwm1offset=50;
pwm2offset=50;
pwm1maximum=255;
pwm2maximum=255;
pwm1divider=0.8039;
pwm2divider=0.8039;
EEPROM.write(23,pwm1offset);
EEPROM.write(24,pwm2offset);
EEPROM.write(25,pwm1maximum);
EEPROM.write(26,pwm2maximum);
if(pwmfrequencydivider != 1 && pwmfrequencydivider != 8)
pwmfrequencydivider=1;
EEPROM.write(27,pwmfrequencydivider);
void ReadEEProm()
int evalue = EEPROM.read(0);
if(evalue != 111) //EEProm was not set before, set default values
WriteEEProm();
return;
FeedbackMin1=ReadEEPRomWord(1);
FeedbackMax1=ReadEEPRomWord(3);
FeedbackPotDeadZone1=EEPROM.read(5);
FeedbackMin2=ReadEEPRomWord(6);
FeedbackMax2=ReadEEPRomWord(8);
FeedbackPotDeadZone2=EEPROM.read(10);
proportional1=double(ReadEEPRomWord(11))/10.000;
integral1=double(ReadEEPRomWord(13))/10.000;
derivative1=double(ReadEEPRomWord(15))/10.000;
proportional2=double(ReadEEPRomWord(17))/10.000;
integral2=double(ReadEEPRomWord(19))/10.000;
derivative2=double(ReadEEPRomWord(21))/10.000;
pwm1offset=EEPROM.read(23);
pwm2offset=EEPROM.read(24);
pwm1maximum=EEPROM.read(25);
pwm2maximum=EEPROM.read(26);
pwm1offset=50;
pwm2offset=50;
pwm1maximum=255;
pwm2maximum=255;
pwm1divider=0.8039;
pwm2divider=0.8039;
else
pwmfloat=float(pwm1maximum-pwm1offset);
pwm1divider=pwmfloat/255.000;
pwmfloat=float(pwm2maximum-pwm2offset);
pwm2divider=pwmfloat/255.000;
pwmfrequencydivider=EEPROM.read(27);
quarter1=float(FeedbackMax1-FeedbackMin1)/4.000;
quarter2=float(FeedbackMax2-FeedbackMin2)/4.000;
threequarter1=quarter1*3.000;
threequarter2=quarter1*3.000;
setPwmFrequency(rmpwmpin, pwmfrequencydivider);
setPwmFrequency(lmpwmpin, pwmfrequencydivider);
void SendAnalogueFeedback(int analogue1, int analogue2)
high=analogue1/256;
low=analogue1-(high*256);
Serial.write('X');
Serial.write(200);
Serial.write(high);
Serial.write(low);
high=analogue2/256;
low=analogue2-(high*256);
Serial.write(high);
Serial.write(low);
void SendPidCount()
unsigned long value=pidcount;
hhigh=value/16777216;
value=value-(hhigh*16777216);
hlow=value/65536;
value=value-(hlow*65536);
lhigh=value/256;
llow=value-(lhigh*256);
Serial.write('X');
Serial.write(201);
Serial.write(int(hhigh));
Serial.write(int(hlow));
Serial.write(int(lhigh));
Serial.write(int(llow));
Serial.write(errorcount);
void SendDebugValues()
//The double is transformed into a integer * 10 !!!
int doubletransfere=int(double(debugdouble*10.000));
Serial.write('X');
Serial.write(211);
Serial.write(debugbyte);
Serial.write(HIGHBYTE(debuginteger));
Serial.write(LOWBYTE(debuginteger));
Serial.write(HIGHBYTE(doubletransfere));
Serial.write(LOWBYTE(doubletransfere));
void SendFirmwareVersion()
Serial.write('X');
Serial.write('-');
Serial.write('P');
Serial.write('I');
Serial.write('D');
Serial.write(' ');
Serial.write(48+firmaware_version_mayor);
Serial.write('.');
Serial.write(48+firmware_version_minor);
void EEPromToSerial(int eeprom_address)
int retvalue=EEPROM.read(eeprom_address);
Serial.write('X');
Serial.write(204);
Serial.write(retvalue);
void ClearEEProm()
for(int z=0; z < 1024; z++)
EEPROM.write(z,255);
void ParseCommand()
if(commandbuffer[0]==1) //Set motor 1 position to High and Low value 0 to 1023
target1=(commandbuffer[1]*256)+commandbuffer[2];
disable=0;
return;
if(commandbuffer[0]==2) //Set motor 2 position to High and Low value 0 to 1023
target2=(commandbuffer[1]*256)+commandbuffer[2];
disable=0;
return;
if(commandbuffer[0]==200) //Send both analogue feedback raw values
SendAnalogueFeedback(currentanalogue1, currentanalogue2);
return;
if(commandbuffer[0]==201) //Send PID count
SendPidCount();
return;
if(commandbuffer[0]==202) //Send Firmware Version
SendFirmwareVersion();
return;
if(commandbuffer[0]==203) //Write EEPROM
EEPROM.write(commandbuffer[1],uint8_t(commandbuffer[2]));
return;
if(commandbuffer[0]==204) //Read EEPROM
EEPromToSerial(commandbuffer[1]);
return;
if(commandbuffer[0]==205) //Clear EEPROM
ClearEEProm();
return;
if(commandbuffer[0]==206) //Reread the whole EEPRom and store settings into fitting variables
ReadEEProm();
return;
if(commandbuffer[0]==207 || commandbuffer[0]==208) //Disable power on both motor
analogWrite(PWMPinM1, 0);
UnsetMotor1Inp1();
UnsetMotor1Inp2();
analogWrite(PWMPinM2, 0);
UnsetMotor2Inp1();
UnsetMotor2Inp2();
disable=1;
return;
if(commandbuffer[0]==209 || commandbuffer[0]==210) //Enable power on both motor
analogWrite(PWMPinM1, 128);
UnsetMotor1Inp1();
UnsetMotor1Inp2();
analogWrite(PWMPinM2, 128);
UnsetMotor2Inp1();
UnsetMotor2Inp2();
disable=0;
return;
if(commandbuffer[0]==211) //Send all debug values
SendDebugValues();
return;
void FeedbackPotWorker()
currentanalogue1 = analogRead(FeedbackPin1);
currentanalogue2 = analogRead(FeedbackPin2);
//Notice: Minimum and maximum scaling calculation is done in the PC plugin with faster float support
bool CheckChecksum() //Atmel chips have a comport error rate of 2%, so we need here a checksum
byte checksum=0;
for(int z=0; z < 3; z++)
byte val=commandbuffer[z];
checksum ^= val;
if(checksum==commandbuffer[3]){return true;}
return false;
void SerialWorker()
while(Serial.available())
if(buffercount==-1)
buffer = Serial.read();
if(buffer != 'X'){buffercount=-1;}else{buffercount=0;}
else
commandbuffer[buffercount]=buffer;
buffercount++;
if(buffercount > 3)
if(CheckChecksum()==true){ParseCommand();}else{errorcount++;}
buffercount=-1;
void CalculateVirtualTarget()
if(turn360motor1==true)
virtualtarget1=target1;
if(currentanalogue1 > int(threequarter1) && target1 < int(quarter1)){virtualtarget1+=FeedbackMax1;}
else{if(currentanalogue1 < int(quarter1) && target1 > int(threequarter1)){virtualtarget1=0-FeedbackMax1-target1;}}
else
if(turn360motor2==true)
virtualtarget2=target2;
if(currentanalogue2 > int(threequarter2) && target2 < int(quarter2)){virtualtarget2+=FeedbackMax2;}
else{if(currentanalogue2 < int(quarter2) && target2 > int(threequarter2)){virtualtarget2=0-FeedbackMax2-target2;}}
else
int updateMotor1Pid(int targetPosition, int currentPosition)
float error = (float)targetPosition - (float)currentPosition;
float pTerm_motor_R = proportional1 * error;
integrated_motor_1_error += error;
float iTerm_motor_R = integral1 * constrain(integrated_motor_1_error, -GUARD_MOTOR_1_GAIN, GUARD_MOTOR_1_GAIN);
float dTerm_motor_R = derivative1 * (error - last_motor_1_error);
last_motor_1_error = error;
return constrain(K_motor_1*(pTerm_motor_R + iTerm_motor_R + dTerm_motor_R), -255, 255);
int updateMotor2Pid(int targetPosition, int currentPosition)
float pTerm_motor_L = proportional2 * error;
integrated_motor_2_error += error;
float iTerm_motor_L = integral2 * constrain(integrated_motor_2_error, -GUARD_MOTOR_2_GAIN, GUARD_MOTOR_2_GAIN);
float dTerm_motor_L = derivative2 * (error - last_motor_2_error);
last_motor_2_error = error;
return constrain(K_motor_2*(pTerm_motor_L + iTerm_motor_L + dTerm_motor_L), -255, 255);
void CalculatePID()
OutputM1=updateMotor1Pid(virtualtarget1,currentanalogue1);
OutputM2=updateMotor2Pid(virtualtarget2,currentanalogue2);
void Motors()
digitalWrite(lmbrkpin,lmbrake>0); // if left brake>0 then engage electronic braking for left motor
digitalWrite(lmdirpin,lmspeed>0); // if left speed>0 then left motor direction is forward else reverse
analogWrite (lmpwmpin,abs(lmspeed)); // set left PWM to absolute value of left speed - if brake is engaged then PWM controls braking
if(lmbrake>0 && lmspeed==0) lmenc=0; // if left brake is enabled and left speed=0 then reset left encoder counter
digitalWrite(rmbrkpin,rmbrake>0); // if right brake>0 then engage electronic braking for right motor
digitalWrite(rmdirpin,rmspeed>0); // if right speed>0 then right motor direction is forward else reverse
analogWrite (rmpwmpin,abs(rmspeed)); // set right PWM to absolute value of right speed - if brake is engaged then PWM controls braking
if(rmbrake>0 && rmspeed==0) rmenc=0; // if right brake is enabled and right speed=0 then reset right encoder counter
void MotorBeep(byte beeps)
digitalWrite(lmbrkpin,0); // ensure breaks are off
digitalWrite(rmbrkpin,0);
for(int b=0;b<beeps;b++) // loop to generate multiple beeps
for(int duration=0;duration<400;duration++) // generate 2kHz tone for 200mS
digitalWrite(lmdirpin,1); // drive left motor forward
digitalWrite(rmdirpin,1); // drive right motor forward
digitalWrite(lmpwmpin,1); // left motor at 100%
digitalWrite(rmpwmpin,1); // right motor at 100%
delayMicroseconds(50); // limit full power to 50uS
digitalWrite(lmpwmpin,0); // shutdown left motor
digitalWrite(rmpwmpin,0); // shutdown right motor
delayMicroseconds(200); // wait aditional 200uS to generate 2kHz tone
digitalWrite(lmdirpin,0); // drive left motor backward
digitalWrite(rmdirpin,0); // drive right motor backward
delay(200); // pause for 200mS (1/5th of a second) between beeps
void loop()
//Read all stored PID and Feedback settings
ReadEEProm();
//Program loop
while (1==1) //Important hack: Use this own real time loop code without arduino framework delays
FeedbackPotWorker();
SerialWorker();
CalculateVirtualTarget();
CalculatePID();
CalculateMotorDirection();
if(disable==0)
SetPWM();
SetHBridgeControl();
pidcount++;